Doing a small coordination study. Info from the transformer manufacturer is the typical x12 inrush for .1 sec and x25 inrush for .01 seconds.
I believe in the x12 inrush.
I understand the x25 is possible but my question is how likely will it be a factor when coordinating the instantaneous regions of a LV breaker?
we are looking at a L-frame SqD breaker with 5.3 micrologic trip unit. The bottom of the instantaneous curve is right on .01 seconds. Should the instantaneous pickup be slid out past the x25 mark? There is not instantaneous delay for the breaker and it can't be cut off.
I believe in the x12 inrush.
I understand the x25 is possible but my question is how likely will it be a factor when coordinating the instantaneous regions of a LV breaker?
we are looking at a L-frame SqD breaker with 5.3 micrologic trip unit. The bottom of the instantaneous curve is right on .01 seconds. Should the instantaneous pickup be slid out past the x25 mark? There is not instantaneous delay for the breaker and it can't be cut off.