I have a control cabinet which is using a 3kVA 480V to 240V single phase transformer to provide power to several control relays in order to power field solenoid devices. The relays are set up such that a PLC fires two relays, a "solenoid relay" and "master relay" at the same time in order to provide power to the field soleniod when needed. After the master relay there is a 240V bridge rectifier in order to convert the AC power to DC to power the solenoids. The master relay is used to provide power from the transformer to the rectifier and then through the appropriate solenoid relay in order to provied power to the solenoid.
The 3kVA transformer has a 10A circuit breaker as well as 10A instantaneous fuses on its primary. We keep blowing the primary fuses for some reason during operation of the relays. The secondary side of the transformer does not supply power unless two of the relays mentioned above are pulled in, and this only lasts for about 500ms or so.
My questions is, when the two relays get pulled in, does this present an inrush to the secondary and primary of the transformer? When trying to measure current on the primary it is hard to get an accurate reading because everything is happening so fast, but using a fluke meter I was seeing 12 and 13A on the primary. With a 3kVA transformer I would expect to see 6.2A on the primary. Why was I seeing 12 and 13A on the primary, was this due to an inrush on the primary of the transformer? What size primary fuse should be used on a 3kVA transformer?
I know this is confusing but I would appreciate any help.
The 3kVA transformer has a 10A circuit breaker as well as 10A instantaneous fuses on its primary. We keep blowing the primary fuses for some reason during operation of the relays. The secondary side of the transformer does not supply power unless two of the relays mentioned above are pulled in, and this only lasts for about 500ms or so.
My questions is, when the two relays get pulled in, does this present an inrush to the secondary and primary of the transformer? When trying to measure current on the primary it is hard to get an accurate reading because everything is happening so fast, but using a fluke meter I was seeing 12 and 13A on the primary. With a 3kVA transformer I would expect to see 6.2A on the primary. Why was I seeing 12 and 13A on the primary, was this due to an inrush on the primary of the transformer? What size primary fuse should be used on a 3kVA transformer?
I know this is confusing but I would appreciate any help.