Junior plan reviewer
I have transformer provided with the switchboard cabinet 480v to 208/120V 30kva. Would the NEC 2017 section 250.30(a)(4) cover the grounding electrode and grounding electrode conductor size for the transformer or is this something not in Nec scope?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I have transformer provided with the switchboard cabinet 480v to 208/120V 30kva. Would the NEC 2017 section 250.30(a)(4) cover the grounding electrode and grounding electrode conductor size for the transformer or is this something not in Nec scope?
why would it not apply? It is a SDS that requires a GES. it is no different than an MCC or industrial control panel that has such a transformer.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Agree. NEC applies including 250.30 and, if applicable, the exception to (A)(4)
 