I went to a job today to check a ground current issue on a new UPS, they were measuring 15.6 amps on a ground conductor. The UPS is 480/480 3-wire with a factory supplied 480 delta to 208/120 wye 150 kva shielded isolation transformer. So I am told I could not verify the transformer type.
There is a ground jumper from the frame of the transformer the bottom of a ground bar, from the ground bar there is a bond jumper to a Ground bar in the UPS and then from the ground bar in the UPS there is a bond jumper back to the top of the ground bar in the transformer cabinet. Current seems to be circulating on the from the transformer frame to the UPS ground bar and back to the transformer.
No load on the secondary, Primary current 15/11/8. With 70% load on the transformer and the ground current went to 22 amps. Utilized a resistive load.
Results were the same with the UPS on and with the UPS in bypass and the UPS off.
Removed the top bond jumper in the transformer to the UPS ground bar and current was still on the bottom jumper in the transformer.
The ground bars are mounted to the metallic frame of the transformer and UPS, so the effect is the same with or without the top ground jumper.
No measurable current on the grounding electrode conductor, Neutral-Ground Bond or any EGCs
Any thoughts?
There is a ground jumper from the frame of the transformer the bottom of a ground bar, from the ground bar there is a bond jumper to a Ground bar in the UPS and then from the ground bar in the UPS there is a bond jumper back to the top of the ground bar in the transformer cabinet. Current seems to be circulating on the from the transformer frame to the UPS ground bar and back to the transformer.
No load on the secondary, Primary current 15/11/8. With 70% load on the transformer and the ground current went to 22 amps. Utilized a resistive load.
Results were the same with the UPS on and with the UPS in bypass and the UPS off.
Removed the top bond jumper in the transformer to the UPS ground bar and current was still on the bottom jumper in the transformer.
The ground bars are mounted to the metallic frame of the transformer and UPS, so the effect is the same with or without the top ground jumper.
No measurable current on the grounding electrode conductor, Neutral-Ground Bond or any EGCs
Any thoughts?