Transformer Issues

Status
Not open for further replies.

laketime

Senior Member
We installed a 75kva 120/208 primary to 120/240v secondary and our phase to neutral reading is 136v and phase to phase is 238v after tapping all the way down. Incoming is 125v phase to neutral and 214v phase to phase. My thoughts are we have utility drop their incoming phase to neutral if possible. Thoughts?
 

laketime

Senior Member
Your measured 136V phase to neutral voltage sounds like a wye secondary instead of a high leg delta secondary.
Just talked to my journeyman and the secondary is wye in the field. The cut sheet I was holding said it was supposed to be delta secondary.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
We installed a 75kva 120/208 primary to 120/240v secondary and our phase to neutral reading is 136v and phase to phase is 238v after tapping all the way down. Incoming is 125v phase to neutral and 214v phase to phase. My thoughts are we have utility drop their incoming phase to neutral if possible. Thoughts?
Why???
You already have the proper nominal output voltage. What else are you expecting?
 