Transformer K- Factor For hospital project

Status
Not open for further replies.

Sajid khan

Senior Member
Location
Pakistan
Dear Forum Members,

What is the recommended K-Factor of the transformer used for hospital project where there are a lot of harmonic generating medical equipments are used?
Our specification is not specifying any rating of K-factor for transformer and the manufacturer is specifying in the fabrication drawings K-factor=1 which i think is not suitable for hospital project.
I have to comments on the fabrication drawings to specify the correct K- Factor tramsformer.

Valueable feedbacks are awaited.

Thanks

Sent from my GT-I9300I using Tapatalk
 
1. How do you know the equipment will result in harmonic distortion?
2. Have you checked with the equipment suppliers as most new equipment has or can be order with built in harmonic mitigation?
3. What percentage of load do you expect the K1 transformers to carry in normal operation?

In the hospitals I have worked in K1 off the shelf transformers are the norm, with a higher K-rated transformer for specific equipment.
 
1. How do you know the equipment will result in harmonic distortion?
2. Have you checked with the equipment suppliers as most new equipment has or can be order with built in harmonic mitigation?
3. What percentage of load do you expect the K1 transformers to carry in normal operation?

In the hospitals I have worked in K1 off the shelf transformers are the norm, with a higher K-rated transformer for specific equipment.

1) The medical consultant told that most of the medical equipments are with harmonic mitigation filters while there are still some equipment which are without filters.
2) same as 1
3) Our substations are double ended substation and loaded 50% only in normal case. It will run on full capacity when the bus tie is closed at the time of one transformer failure.

One more thing is that we have capacitor banks with harmonic filter in each substations. Will it substitute the requirement of K-factor=1 rated transformers for harmonic mitigation?
 
You should consider the cap banks with harmonic filters.

With that:

K4 up to 65% nonlinear load
K13 50-95% non-linear
K20/30 95%+ (not commonly used)
Harmonic mitigating when primarily nonlinear and very sensitive equipment above 65% non-linear
 
Also, it is most common: if you decide transformers need K rating, size the neutral 200% on the secondary of the xfrm at least up to the first disconnect.
 
In the hospitals I have worked in K1 off the shelf transformers are the norm, with a higher K-rated transformer for specific equipment.
Same here. Specialized equipment such as radiology typically have there own isolation transformers engineered for their own problems.

Roger
 
Also, it is most common: if you decide transformers need K rating, size the neutral 200% on the secondary of the xfrm at least up to the first disconnect.
I have found this not to be common anymore. K rated implies the expectation of harmonics. neutrals beyond 100% imply triplin harmonics part the capacity of the neutral.

Oversized neutrals in my experience over the last bunch of years seemed to have gone the way of the isolated ground receptacles.

15 years ago, that was a different story.
 
From the discussion above i concludes that transformer with k-factor=1 will b workable fine for hospital when other harmonic mitigating filters are there in the system.

Sent from my GT-I9300I using Tapatalk
 