Re: Transformer KVA
This is not as simple as it looks:
The 3-phase loading is a no brainer--25KVA/3 for each, Ta, Tb, & Tc.
Now let Ta be directly connected to the 1-phase load, then, the load current, Isp, divides 2:1 between Ta and the other two. Then the apparent power computations are,
Pa = 240 x Isp*2/3 for the first
Pb = Pc = 240 x Isp*1/3 each for Tb & Tc.
Pb + Pc = 240 x Isp*2/3 for both
Ta provides half the apparent power,
Tb & Tc provide one quarter each.
You must consider each individual transformer when you have such an unbalanced load.