dnbob
Senior Member
- Location
- Rochester, MN
I have an old (1972) 150 KVA 480D to 208Y120 3 phase transformer.
The primary current idling with no secondary load is Phase A 3 amps, Phase B 3 Amps, Phase C 4 amps.
To find out what this is costing to run, with no load, is this the correct formula
Phase Amps (3+3+4) = 10 amps * 480 * 1.73 = 8,304 watts/1000 - 8.304 KW * 24 hours per day * $.11/KWH = 8.304*24*.11 = $21.92 in energy use per day?