P PatLock New User Location Las Vegas Occupation I&C Lead Aug 7, 2022 #1 I am installing a 192kva service and stepping down from 480 primary to 277 secondary. Can I do 320 amp on each leg?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 7, 2022 #2 How are you deriving that number ??
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 7, 2022 #3 Single phase 277 volts? Often the 480 volt system would be a 480Y/277 volt system. 480 line to line and 277 line to neutral. What exactly are you trying to accomplish?
G ggunn PE (Electrical), NABCEP certified Location Austin, TX, USA Occupation Consulting Electrical Engineer - Photovoltaic Systems Aug 7, 2022 #4 PatLock said: Can I do 320 amp on each leg? Click to expand... What does that mean?
TwoBlocked Senior Member Location Bradford County, PA Occupation Industrial Electrician Aug 7, 2022 #5 How do you make tiger soup? First catch the tiger. How do you step down 192kva 480 primary to 277 secondary at 320 amps? First find the transformer. But really, they do make impedance transformers to do that. Reduces arc flash, you know. But I don't think the numbers work...
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Aug 7, 2022 #6 Tiger soup. I like that.
M marcosgue Senior Member Location Tampa Occupation Electrician Aug 7, 2022 #7 320Ax480Vx1.732=266kva v.s 192kva might be 192kva/480Vx1.732=231A I think you type the wrong number 320A instead 230A
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Aug 8, 2022 #8 ptonsparky said: Tiger soup. I like that. Click to expand... It is very delicious, but I try not to eat it as tigers are endangered .
R robertd Senior Member Location Maryland Occupation electrical contractor Aug 11, 2022 #9 Is it a delta to Y transformer?