Hello,
From what I have gleaned from extensive google-fu, i have found the following to be a possible code compliant transformer installation, my questions will be posed after:
75KVA 480D - 120/208Y
Primary OCPD:
75000 / (480x1.732) = 90.21A ----------> 90.21A x 1.25 = 112.76A --------> Next size up = 125A OCPD
Secondary OCPD (Transformer will feed panelboard with branch circuits):
75000 / (208x1.732) = 208.19A -----------> (assuming continuous load is 100% of transformer rating) 208.19 x 1.25 = 260.23A ---------> Next size up = 300A OCPD
---------------------------------------------------------------------------------------------------------------
If what i've suggested above is correct, and one can provide a 300 amp panelboard from a 75KVA transformer, is it then kosher to load this panel up to 80%, which would be 240A/phase and approximately 15% overload of the 75KVA transformer rating? I want to say no, because the load was only calculated for a 75KVA transformer, but i could see people in the field seeing a 300 amp panel with room to spare and not considering the load on the transformer.
I guess i'm also having trouble understanding the usable KVA that can be loaded on a transformer vs. acceptable OCPD.
From what I have gleaned from extensive google-fu, i have found the following to be a possible code compliant transformer installation, my questions will be posed after:
75KVA 480D - 120/208Y
Primary OCPD:
75000 / (480x1.732) = 90.21A ----------> 90.21A x 1.25 = 112.76A --------> Next size up = 125A OCPD
Secondary OCPD (Transformer will feed panelboard with branch circuits):
75000 / (208x1.732) = 208.19A -----------> (assuming continuous load is 100% of transformer rating) 208.19 x 1.25 = 260.23A ---------> Next size up = 300A OCPD
---------------------------------------------------------------------------------------------------------------
If what i've suggested above is correct, and one can provide a 300 amp panelboard from a 75KVA transformer, is it then kosher to load this panel up to 80%, which would be 240A/phase and approximately 15% overload of the 75KVA transformer rating? I want to say no, because the load was only calculated for a 75KVA transformer, but i could see people in the field seeing a 300 amp panel with room to spare and not considering the load on the transformer.
I guess i'm also having trouble understanding the usable KVA that can be loaded on a transformer vs. acceptable OCPD.