jdsmith said:If you're the utility you size them conservatively at the beginning and eventually load them to 105%:roll:
jdsmith said:If you're the utility you size them conservatively at the beginning and eventually load them to 105%:roll:[/quote/]
I think you may be dislexic and meant to type 150%![]()
pes said:what is the rule of thumb when it comes to loading a 3 phase 480 transformer or any tranformer. ie.. KVA30 480v 3phase HV amps 36 / LV amps 83. how high can I load??
drbond24 said:The rule of thumb for loading a transformer is that the hotter it gets the shorter its life will be. They will operate just fine above their rating by quite a bit, but the more you do it the faster it ages. Temperature = age.
weressl said:Actually the rule of thumb for insulation life is more specific.
You will halve the life of insulation for every 10C* rise.
drbond24 said:You are correct. I was being general on purpose.![]()
weressl said:Actually the rule of thumb for insulation life is more specific.
You will halve the life of insulation for every 10C* rise.