Transformer: Location and Clearance Requirements

Status
Not open for further replies.

zam

Member
Location
New York, NY
This is regarding a 30 kVA dry-type transformer that needs to me installed in a small retail store in Honolulu, Hawaii. As per the NEC, can a transformer be installed in the restroom? What are the clearance requirements for a transformer, both floor mounted and ceiling mounted. Thank you.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is regarding a 30 kVA dry-type transformer that needs to me installed in a small retail store in Honolulu, Hawaii. As per the NEC, can a transformer be installed in the restroom? What are the clearance requirements for a transformer, both floor mounted and ceiling mounted. Thank you.

Just follow the transformer manufacturers clearances, typically 6" or 12" from the wall to provide proper ventilation.
 