Hello all,
I have a customer with an unoccupied commercial space that still has an electric bill of about $250 a month. All of the HVAC is off as well as water heaters, lights, etc. The only thing I can see running is a few exit/emergency lights, an electronic door lock, ...and several transformers.
There are three 480--208 stepdown transformers constantly humming along. I took readings on the primary side of each in their normal
(almost no)load state and with completely no load.
With absolutely no load, I had:
75kVA with an average 3.8A per phase, another 75kVA with an average 4.1A per phase, and a 150kVA with an average 9.2A per phase
(they are all delta-wye, 150° rise)
First, is this normal?
My understanding is that transformers typically run best at around 50-60% load, and I've have been reading-up on no load losses. I've read several other threads here with differing estimates. My observations seem to be at about 5-6% loss.
Second, are there any suggestions to alleviate the situation other than just shutting off the feeds to the transformers?
Lastly, I'd appreciate any help on the math of converting these per-phase amp readings to kWh in order to confirm that these transformer losses are causing the high bill. The only way I can get it close to $250/month is with a power factor of 0.1.
Averages: 3.8+4.1+9.2=17.1A
P = 3 (VL-N) (I) (Pf)
3 (284V) (17.1A) (0.1) = 1457W = 1.45kW
1.45kW * 3 phases = 4.35kW
4.35kW * 24hr * 30day = 3132kWh/month
3132kWh * $0.08 = $250
It seems like I'm fudging things low with assuming a power factor of 0.1 and 8¢/kWh. I'm a better practical troubleshooter than a mathematical one!
Thanks everybody.
I have a customer with an unoccupied commercial space that still has an electric bill of about $250 a month. All of the HVAC is off as well as water heaters, lights, etc. The only thing I can see running is a few exit/emergency lights, an electronic door lock, ...and several transformers.
There are three 480--208 stepdown transformers constantly humming along. I took readings on the primary side of each in their normal
(almost no)load state and with completely no load.
With absolutely no load, I had:
75kVA with an average 3.8A per phase, another 75kVA with an average 4.1A per phase, and a 150kVA with an average 9.2A per phase
(they are all delta-wye, 150° rise)
First, is this normal?
My understanding is that transformers typically run best at around 50-60% load, and I've have been reading-up on no load losses. I've read several other threads here with differing estimates. My observations seem to be at about 5-6% loss.
Second, are there any suggestions to alleviate the situation other than just shutting off the feeds to the transformers?
Lastly, I'd appreciate any help on the math of converting these per-phase amp readings to kWh in order to confirm that these transformer losses are causing the high bill. The only way I can get it close to $250/month is with a power factor of 0.1.
Averages: 3.8+4.1+9.2=17.1A
P = 3 (VL-N) (I) (Pf)
3 (284V) (17.1A) (0.1) = 1457W = 1.45kW
1.45kW * 3 phases = 4.35kW
4.35kW * 24hr * 30day = 3132kWh/month
3132kWh * $0.08 = $250
It seems like I'm fudging things low with assuming a power factor of 0.1 and 8¢/kWh. I'm a better practical troubleshooter than a mathematical one!
Thanks everybody.