Just double checking my math, I saw this transformer hookup and it appears the breakers are too large to protect it.
this is a 112.5 KVA 480 primary 208 secondary 3 phase. The primary is 175 amp breaker and the secondary is 400 amp.
Even though you can go to the next size up on breaker ocd on the primary, I thought if you went over 1.25 (regardless of next size up) that you had to put the secondary at 1.25 to ensure proper protection.
Am I correct on this?? Is this transformer installed wrong??
this is a 112.5 KVA 480 primary 208 secondary 3 phase. The primary is 175 amp breaker and the secondary is 400 amp.
Even though you can go to the next size up on breaker ocd on the primary, I thought if you went over 1.25 (regardless of next size up) that you had to put the secondary at 1.25 to ensure proper protection.
Am I correct on this?? Is this transformer installed wrong??