travish
Member
- Location
- Central North Carolina
- Occupation
- Electrician
installed a GE 150kva xformer today delta - delta 480 to 240 mid tap neutral connection on the secondary. Note on the neutral wire says kva of neutral is 0.05% of xformer kva rating. the wire at the neutral tap looked like a #8 awg. only running 3 phase loads so I will not have any current on the nuetral anyway. Here is my question
Hypothetical lets say 4/0 conductors on the secondary feeding a panel 25 ft away. somebody runs a forklift into the conduit feeding the panel. Only 1 phase shorts to ground. Can a #8 wire carry enough fault current to trip the primary or would it burnout like a fuse?
Looks like to me the manufacture would be required to provide a large enough neutral connection to carry the fault current availible from the xxformer
anybody got any thoughts on this?
Travis
Hypothetical lets say 4/0 conductors on the secondary feeding a panel 25 ft away. somebody runs a forklift into the conduit feeding the panel. Only 1 phase shorts to ground. Can a #8 wire carry enough fault current to trip the primary or would it burnout like a fuse?
Looks like to me the manufacture would be required to provide a large enough neutral connection to carry the fault current availible from the xxformer
anybody got any thoughts on this?
Travis