I have a station class transformer, 5MVA. In service for three weeks and the nitrogen pressure fell to zero. Gauge needle didn’t go up or down after it hit zero and ambient temp changed. Top oil runs 40C with load fairly constant. Added nitrogen and could not charge past 3psi.Remove feed and pressure would fall to 1.5 and over the next one or two days the gauge would read zero again. This was repeated several times over the next month. Each time the results were the same. I can’t get a clearance on the transformer and the nitrogen blanket is important to me to keep the moisture out of the transformer. During each nitrogen fill, when the pressure was at 3psi, ultrasound suggested the leak was coming from the X1 bushing. Transformer has remained energized during all nitrogen adds.
An external nitrogen regulation system was added that keeps pressure above .5 psi and bleeds off at 5 psi. Since that system was added, the transformer tank pressure has remained positive and the nitrogen bottle pressure has remained constant indicating no gas leak.
Ambient here has been 30-50F.
I cannot explain why the regulation system has worked for the last two weeks and not emptied the nitrogen bottle. Any ideas?
An external nitrogen regulation system was added that keeps pressure above .5 psi and bleeds off at 5 psi. Since that system was added, the transformer tank pressure has remained positive and the nitrogen bottle pressure has remained constant indicating no gas leak.
Ambient here has been 30-50F.
I cannot explain why the regulation system has worked for the last two weeks and not emptied the nitrogen bottle. Any ideas?