We are examining a couple 400kva 480pri/208/120sec transformers that are quite old and I suspect drinking up energy with no load losses.
Curious what you guys usually see as reasonable loss for modern transformers? I have not checked one in a long time because they always have loads but if memory serves, I think about 1% of the KVA rating?
in any case, I have tested these in two ways. Either use my meters to determine PF, then calc the amps and volts, or use the 3P KW feature on my meter which is assessing all 3 legs, current on one, and PF.
Curious what you guys usually see as reasonable loss for modern transformers? I have not checked one in a long time because they always have loads but if memory serves, I think about 1% of the KVA rating?
in any case, I have tested these in two ways. Either use my meters to determine PF, then calc the amps and volts, or use the 3P KW feature on my meter which is assessing all 3 legs, current on one, and PF.