I have a customer who has a 200 amp single phase 120/240 service who wants to add 3 480 volt machines, 1 rated at 71 amps, 1 at 48 amps, and 1 at 46.5 amps, he has a 112.5 kva transformer with 120/208 primary and 277/480 secondary's he wants me to install for the equipment, I have several questions regarding this installation, do I have to feed the transformer at its kva rating or the actual load connected to it, I want to build a new 400 amp 3 phase service leaving the existing 200 amp single phase disconnect and panel as is, and add a 200 amp 3 phase disconnect to feed the transformer covering the load rather than with a 400 to cover the kva rating, is this code compliant? I will install a 200 amp mcb panel on the secondary side to feed the machines. Thanks