New PV site. Let's say I have a 1MVA transformer and (10) 150kW inverters, but the inverters are all de-rated to 100kW on this LV side which is 600V.
The exception in 705.65(B) makes me think that I don't need a main breaker on the 600V side since the de-rated continuous current of the inverters does not exceed transformer rating (1MVA transformer... 10 x 100kW also = 1MVA).
What's giving me pause is that the exception only works in my favor to not need a main breaker if I'm allowed the use the de-rated value. With the standard rated value of the inverter, I'd need a main. It also says inverter (singular). Anybody know if I can use the de-rated value for this?
=== 705.65(B)===
Exception: A power transformer with a current rating on the side connected toward the interactive inverter output that is not less than the rated continuous output current of the inverter shall be permitted without overcurrent protection from that source.
===
Lastly, the whole evaluating both sides as primary trips me up, as I believe it does for many others else as well. It is not a problem that I'll have 10 CBs on the 600V side? And the sum of those CB ratings will total beyond the 125% that is permitted for if it were one device. Is that all irrelevant due to 705.65?
=== Note 2 from 450.3(A).. my underlines===
Where secondary overcurrent protection is required, the secondary overcurrent device shall be permitted to consist of not more than six circuit breakers or six sets of fuses grouped in one location. Where multiple overcurrent devices are utilized, the total of all the device ratings shall not exceed the allowed value of a single overcurrent device. If both circuit breakers and fuses are used as the overcurrent device, the total of the device ratings shall not exceed that allowed for fuses.
======================
The exception in 705.65(B) makes me think that I don't need a main breaker on the 600V side since the de-rated continuous current of the inverters does not exceed transformer rating (1MVA transformer... 10 x 100kW also = 1MVA).
What's giving me pause is that the exception only works in my favor to not need a main breaker if I'm allowed the use the de-rated value. With the standard rated value of the inverter, I'd need a main. It also says inverter (singular). Anybody know if I can use the de-rated value for this?
=== 705.65(B)===
Exception: A power transformer with a current rating on the side connected toward the interactive inverter output that is not less than the rated continuous output current of the inverter shall be permitted without overcurrent protection from that source.
===
Lastly, the whole evaluating both sides as primary trips me up, as I believe it does for many others else as well. It is not a problem that I'll have 10 CBs on the 600V side? And the sum of those CB ratings will total beyond the 125% that is permitted for if it were one device. Is that all irrelevant due to 705.65?
=== Note 2 from 450.3(A).. my underlines===
Where secondary overcurrent protection is required, the secondary overcurrent device shall be permitted to consist of not more than six circuit breakers or six sets of fuses grouped in one location. Where multiple overcurrent devices are utilized, the total of all the device ratings shall not exceed the allowed value of a single overcurrent device. If both circuit breakers and fuses are used as the overcurrent device, the total of the device ratings shall not exceed that allowed for fuses.
======================