Table 450.3 indicates MAXIMUM rating or setting of transformer primary/secondary OCPD. Is it acceptable for the OCPD on either side of the transformer be LESS than the listed MAXIMUMS in table 450.3 by a percentage of say 20%, plus or minus? Best practice would be to size to MAXIMUM, but any other technical implications or code implications to consider sizing to a smaller percentage than the table indicates? Practically speaking, it's my understanding start-up or in-rush current is something to consider, but it could be upwards of +/-6x FLA anyways, so a 20% smaller OCPD should not trip due to inrush? Thanks all.