Howdy forum, its been awhile since I had to size OCPD for a transformer.
The transformer is feeding a chiller which cools a laser cutter.
The machine is technically not continuous, but I think for the sake of safety, I will size it if it is.
The laser will never run for more then 3 hours, but the chiller could stay on in between jobs so CONTINUOUS.
I have a 208 wye > 480V Delta 75kva transformer. The chiller runs on 480V, 3 phase. The service is 208V.
The full load amps @ 208V are 127. So 127 x 1.25 = 158.75 amps continuous on the 208V side.
The full load amps @ 480V are 55. So 55 x 1.25 = 68.79 amps continuous on the 480V side.
I believe I am correct that I size the primary OCPD to 160Amps. I size the primary wire accordingly.
I was questioning myself that I size it based on the transformer max ampacity, but this is a single dedicated load on that XFMR, only for the chiller.
Location is using NEC 2020.
What I am confused about is section 450.3 of the code.
Its my understanding that based on 240.4(F) since this is neither a 2 wire transformer or a delta>delta transformer, I need OCPD protection on both the
primary and secondary......but then I look at table 450.3(B) and it seems to imply I dont need secondary OCPD if I size the
primary OCPD within 125% or the continuous amps....which is 158.75.......so do I need secondary OCPD?
thanks so much for any help.
The transformer is feeding a chiller which cools a laser cutter.
The machine is technically not continuous, but I think for the sake of safety, I will size it if it is.
The laser will never run for more then 3 hours, but the chiller could stay on in between jobs so CONTINUOUS.
I have a 208 wye > 480V Delta 75kva transformer. The chiller runs on 480V, 3 phase. The service is 208V.
The full load amps @ 208V are 127. So 127 x 1.25 = 158.75 amps continuous on the 208V side.
The full load amps @ 480V are 55. So 55 x 1.25 = 68.79 amps continuous on the 480V side.
I believe I am correct that I size the primary OCPD to 160Amps. I size the primary wire accordingly.
I was questioning myself that I size it based on the transformer max ampacity, but this is a single dedicated load on that XFMR, only for the chiller.
Location is using NEC 2020.
What I am confused about is section 450.3 of the code.
Its my understanding that based on 240.4(F) since this is neither a 2 wire transformer or a delta>delta transformer, I need OCPD protection on both the
primary and secondary......but then I look at table 450.3(B) and it seems to imply I dont need secondary OCPD if I size the
primary OCPD within 125% or the continuous amps....which is 158.75.......so do I need secondary OCPD?
thanks so much for any help.