Looking at installing a European-sourced machine in the shop. It nameplate states 40KW, 64A, 50/60Hz, 3-ph. We're debating the relative merits of a 45KVA vs 75KVA transformer. I'm leaning toward the 75KVA unit, since we may add another 400V machine in the future, and the larger transformer will run cooler.
We have a 240V corner-grounded service in the building, and a spare 225A breaker in the switchgear.
Assuming I go with the 75KVA trafo, do I need additional OCPD beyond the 225A breaker on the primary side of the trafo (240V) if I include secondary OCPD (400V)? I'm looking at an 80A breaker for the secondary (64A x 120% = 76.8A --> 80A). Probably a small 480V main breaker panel, so I have room for additional 400V loads in the future. Do I size the 400V panel's main breaker to the output amperage of the trafo?
I don't do feeder and OCPD sizing for transformers very often, and I'd rather get this right the first time.
Thanks,
SceneryDriver
We have a 240V corner-grounded service in the building, and a spare 225A breaker in the switchgear.
Assuming I go with the 75KVA trafo, do I need additional OCPD beyond the 225A breaker on the primary side of the trafo (240V) if I include secondary OCPD (400V)? I'm looking at an 80A breaker for the secondary (64A x 120% = 76.8A --> 80A). Probably a small 480V main breaker panel, so I have room for additional 400V loads in the future. Do I size the 400V panel's main breaker to the output amperage of the trafo?
I don't do feeder and OCPD sizing for transformers very often, and I'd rather get this right the first time.
Thanks,
SceneryDriver