Re: Transformer OCPD
The maximum protection is letting you know that you can not surpass that max. ie. protect the X-Fmr with a 300amp ocpd just because you happened to have one in the shop, that is why you go thru the calculations, the general rule for transformers rated at600V, nominal or less is to protect the primary windings of the XFmer at not more than 125% of the rated primary current of the X-Fmr, what I gather from Charlies posts is I could just as well protect the X-Fmr with a 20Amp ocpd, will the 50 amp or 20 amp not heat up and trip when the X-Fmr is working due to the load? Would you put a 15 amp breaker on an ac condensor nameplate says Max. OCPD 60amps, what is going to happen in peak summer time weather, just like if the said AC condensor keeps tripping the 60amp do you replace it with a 70amp or 80amp.