Hey guys,
I’m trying to completely wrap my head around transformer OCPD. I was watching a video on the calculations for sizing over current protection, and here is the example presented.
480V single phase primary, 12kva load
120V single phase secondary, 12kva load
With that said the FLA for the secondary is 100 amps, and the primary FLA being 25 amps.
In the explanation, the FLA on the primary was multiplied by 250% the get the maximum OCPD. He then explained that you don’t HAVE to choose maximum OCPD but you can’t go too low because of the influx at the start up of the transformer.
My question is, why would I choose to not use maximum OCPD? Also, how low can I go without causing overcurrent at start up?