According to table 450.3(A)the primary protection using fuses in a supervised location allows maximum setting to be 250% of FLA.
That part is clear. My question is when sizing the conductors 125% of full load amps does not seem like the cable will be properly protected.
The primary of the transformer being used has FLA of 120A. This means I can use a 300A fuse. I am not seeing anywhere in code that calls for the cable to up-sized as well. Should the cable be sized at 125% or at 300%? I must be missing something.
Thanks
That part is clear. My question is when sizing the conductors 125% of full load amps does not seem like the cable will be properly protected.
The primary of the transformer being used has FLA of 120A. This means I can use a 300A fuse. I am not seeing anywhere in code that calls for the cable to up-sized as well. Should the cable be sized at 125% or at 300%? I must be missing something.
Thanks