Are transformers voltage ratings typically +-10%?
Last edited:
Are transformers voltage ratings typically +-10%?
Now, where does this +-10% voltage come from?
I think he may be refering to available tap settings?
Or permissible input voltage tolerance.I think he may be refering to available tap settings?
That is more appropriate for a voltage regulator.Or permissible input voltage tolerance.
If input voltage is higher than highest tap setting, the tranny would likely be overloaded because of higher than rated voltage on secondary.lets say the highest tap setting, can the transformer still handle voltages above the largest tap setting? Is there a % tolerance?
It's appropriate for anything connected to an electrical supply.That is more appropriate for a voltage regulator.
Standard utility delivery voltage is +10%, -15% of nominal.
Utility voltage variation is going to be orders of magnitude greater than the manufacturing tolerance of the turns ratio.
As I understand it Voltages higher than those ratings for the transformer can lead to core saturation. When that happens to the transformer with sease to act as a transformer and the secondary voltage will drop.
Your comments are welcome