When we size an overcurrent protection device for a transformer we always use 125% of the FLA (SEC. side) of the xfrmr. Lets use an example, we have 112.5KVA xfmr, FLA=311.6A(208V),
OCPD=1.25 x 311.6= 389.5A (400A next size-up). Now my question, We know the FLA of this XFMR is 311.6A but we also know we are using 400A OCPD. If we load our 400A MCB panel ,lets say,with 350A connected load,we know that won't trip the breaker instantly, how is the transformer is protected? and we know we are not to exceed the 311A because that will overload the Xfmr?.
any thoughts!!! Thank you
OCPD=1.25 x 311.6= 389.5A (400A next size-up). Now my question, We know the FLA of this XFMR is 311.6A but we also know we are using 400A OCPD. If we load our 400A MCB panel ,lets say,with 350A connected load,we know that won't trip the breaker instantly, how is the transformer is protected? and we know we are not to exceed the 311A because that will overload the Xfmr?.