I have a vendor design I'm reviewing and it has a 10 kVA single-phase transformer being installed. The primary OCPD is 30A, the secondary is connected to a 100A main breaker panel. The panel has 10 branch circuit breakers. The way I read NEC Table 450.3(B) is that I can only have 125% secondary protection, which would be a 60A breaker. In addition, I would think I would need to install #2 AWG conductors from the 10 kVA transformer due to a 100A main panel breaker. So my question is am I reading the code wrong i.e. the secondary OCPD is wrong. This installation will per the NEC not the NESC. In addition, why would the vendor install a 100A breaker when the transformer max amps would be approximately 40A.