Could someone please check my work and let me know if I'm doing this right? Here is what I have:
225A, 480Y/277V panel that feeds a 45kva 480V:208Y/120V transformer that feeds a 125A, 208Y/120V panel
It is my understanding that unless you are feeding a single phase or three phase delta-delta transformer you would size the overcurrent protection for primary & secondary protection based on Table 450.3(b) of the NEC (I'm using 2005 NEC). Table 450.3(b) says I need to size the primary OCPD by 250% (if greater than 9 amps) and the secondary OCPD needs to be sized by 125%.
Following that logic, here is what I get:
Primary OCPD:
45kVA/.831=54.2A*250% (Table 450.3(b))=135.4A
Using the next size up, primary OCPD would be: 150A/3P CB
Secondary OCPD:
45kVA/.36=125A*125% (Table 450.3(b))=156.3A
Using the next size up, secondary OCPD would be: 175A/3P CB
Is this correct? If it is this would mean that I could not use a 125A 208Y/120V panelboard and that I would need to upsize it to a 200A panelboard.
Thanks in advance for your response.
225A, 480Y/277V panel that feeds a 45kva 480V:208Y/120V transformer that feeds a 125A, 208Y/120V panel
It is my understanding that unless you are feeding a single phase or three phase delta-delta transformer you would size the overcurrent protection for primary & secondary protection based on Table 450.3(b) of the NEC (I'm using 2005 NEC). Table 450.3(b) says I need to size the primary OCPD by 250% (if greater than 9 amps) and the secondary OCPD needs to be sized by 125%.
Following that logic, here is what I get:
Primary OCPD:
45kVA/.831=54.2A*250% (Table 450.3(b))=135.4A
Using the next size up, primary OCPD would be: 150A/3P CB
Secondary OCPD:
45kVA/.36=125A*125% (Table 450.3(b))=156.3A
Using the next size up, secondary OCPD would be: 175A/3P CB
Is this correct? If it is this would mean that I could not use a 125A 208Y/120V panelboard and that I would need to upsize it to a 200A panelboard.
Thanks in advance for your response.