transformer overcurrent sizing

Status
Not open for further replies.
sizing overcurrent protection for a 480volt primary, 208/120 secondary transformer when both the primary and secondary will have over current protection,
so based on 450.3(b) should I be using 250% for primary and 125% for secondary? or can I use 125% for both?

my transformer is a 30 kva 480 volt primary and a 208/120 volt secondary.

so based on 450.3(b)

I come up with 50 amp breaker for primary using 125%
and 90 amp breaker using 250% which one is correct?
 

Ingenieur

Senior Member
Location
Earth
sizing overcurrent protection for a 480volt primary, 208/120 secondary transformer when both the primary and secondary will have over current protection,
so based on 450.3(b) should I be using 250% for primary and 125% for secondary? or can I use 125% for both?

my transformer is a 30 kva 480 volt primary and a 208/120 volt secondary.

so based on 450.3(b)

I come up with 50 amp breaker for primary using 125%
and 90 amp breaker using 250% which one is correct?

both are 'correct'
250% is the max
you can go lower, ie 125%, but not higher
too low may cause nuisance tripping when energizing
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Keep in mind your conductor must be protected according to it's ampacity. If you elect to size at 250% you will incur higher cost than 125% due to wire size and possibly higher cost for your over-current device,.
 