I have a 150kva Y-Y 3phase transformer (12470/7200v - 480/277v) thats currently in service. When looking at the meter logs I see 300-400 amp spikes on the secondary side (This transformer serves irrigationn pumps) for 1-2 hour durations, sometimes even longer. Now my first though is that i need to upsize this transformer to a 300kva or 500kva, but when looking at the peak demand at the meter, it reads around 160kw or so each month. Why dont I see the 300-400amp spikes in the demand calc at the meter? How is this demand calculated (I know its calculated by using kwh, but I thought i would see the 300-400 amp peaks in this calculation?)? Should I upsize this transformer based on the 300-400amps the irrigation pumps pull or am i okay since the peak demand calc at the meter reads 160kw peak. The meter is on a 15min interval. The CT ratios for metering is 200/5.