Sorry very basic question:
For phase shift between the Delta and Wye connection transformer. when compared to the HV winding lets say between VAB shall be in phase with Vag on the LV side of the transformer.
However comparison is not among same quantities.
So HV ph to ground is used as comparison. VAG lags behind VAB by 30 deg.
If you put this in phasor rotation VAG leads Vag by 30 degrees.
My question if voltage phasor is measure Vab on LV side will it be in phase with VAB? or it will lag behind by 30 deg with comparison to VAB?
For phase shift between the Delta and Wye connection transformer. when compared to the HV winding lets say between VAB shall be in phase with Vag on the LV side of the transformer.
However comparison is not among same quantities.
So HV ph to ground is used as comparison. VAG lags behind VAB by 30 deg.
If you put this in phasor rotation VAG leads Vag by 30 degrees.
My question if voltage phasor is measure Vab on LV side will it be in phase with VAB? or it will lag behind by 30 deg with comparison to VAB?