is it possible to take a 240V-120V single phase isolation transformer and input 120V to get 60V? Needed in an application of 2.5Kva?
I think SCR control on the primary of a transformer is not a good idea. Actually a bad idea. In my opinion.170203-0838 EST
boptrop:
Apparently you prefer SCR control and that is fine, then there is no need for a Variac at all.
If you only need 60 V, then a a 2 to 1 transformer from a 120 V source is a good choice. This is better than just using 1/2 of a cycle to get an average of 60 V.
An isolation transformer is probably desirable no matter what output voltage you need so that neither input AC line is connected directly to your load.
If you use SCR control thru the transformer, either on the secondary or primary, then you need an SCR control that does not produce an excessive DC component. A DC component forces an unbalance of the magnetic core hysteresis curve and higher saturation current. Some dimmers are listed as suitable for dimming (average voltage adjustment) with a magnetic transformer. Ordinary phase shift dimmers likely have unbalanced turn on times between the positive and negative 1/2 cycles resulting in a DC component.
I agree. However, it is done and Lutron makes dimmers specifically for this purpose.I think SCR control on the primary of a transformer is not a good idea. Actually a bad idea. In my opinion.
What do you mean by "bottom end of SCR module ratings"?And, given the currents involved it is at the bottom end of SCR module ratings so there would be very little point in doing it.
170204-1014 EST
Besoeker2:
I agree. However, it is done and Lutron makes dimmers specifically for this purpose.
http://www.lutron.com/en-US/Education-Training/Pages/LCE/DimmingBasics.aspx
My background is mostly industrial power electronics. Variable speed drives and high current rectifiers.What do you mean by "bottom end of SCR module ratings"?