There has been other post regarding when to use 250% of primary current to protect primary conductors for transformers over 9 amperes or use 125%
I just wanted to make sure I’m understanding this
If my transformer is over 9 amperes (primary side?) then I can size the primary OCPD to to 250% of its rated current? Then size a primar conductor to this ampacity after temperature correction and derating or at 125 % of continuous load?
Then I can size the secondary OCPD to 125% of its rated current? Then size the secondary conductor for this ampacity as above?
However primary only protection at 125 percent only applies to single phase 2 wires in and 2 out or delta delta?
Is this correct?