Do you have a clear picture of the nameplate?I am being told this transformer is for a 2400 delta primary system. This doesnt seem correct. It looks to me like it is meant for a wye system and the second bushing is for loop feed...or am I misinterpreting the bushing numbering scheme???
Do you have a clear picture of the nameplate?
From what I see it looks like a single phase HV primary and a secondary with a center tap on X2.
riFrom what I see it looks like a single phase HV primary and a secondary with a center tap on X2.
Send us a pic of the nameplate.
Unfortunately I have not been able to get a picture of the nameplate, that is the problem. I do not have the unit. I will try further next week.
Yes, I concur. The question is the primary bushing arrangement. I am not a MV guy, but from by experience, H1A and H1B bushings implies it is a loop feed grounded neutral unit. IF it was a delta primary, I would expect the bushings to be H1 and H2 if it was radial feed, or for loop feed H1A and H2A for primary in and H1B and H2B for primary out.. Now that I think about it though, I dont recall ever seeing a small single phase padmount with loop feed bushings....
I've understood what you've been saying, asking all along. I just cannot contribute any information beyond what you've already surmised.... I am a bit surprised no one seems to understand what i am saying. ...
I've understood what you've been saying, asking all along. I just cannot contribute any information beyond what you've already surmised.
Nameplate, nameplate, nameplate!
H1A, H1B, and one side of the primary winding are internally connected... or should be... but I prefer to verify by way of the NAMEPLATE. :happyyes:Do I misunderstand, or does "loop feed" in this context mean that H1A and H1B are internally connected?
Cheers, Wayne
Ok found out that the unit is indeed for a grounded wye not a delta. The second bushing is just a feed thru. His original description was poorly worded. Thanks everyone for your input
Ok found out that the unit is indeed for a grounded wye not a delta. The second bushing is just a feed thru. His original description was poorly worded. Thanks everyone for your input
EB
Not sure how that has to do with this transformer in the pic. Explain feed thru.
Can you draw a diagram of how the system is connected. Sorry if it is elementary to others.
EB
Not sure how that has to do with this transformer in the pic. Explain feed thru.
Can you draw a diagram of how the system is connected. Sorry if it is elementary to others.
All it is saying is the ANSI type 2 is made in those voltage ranges, you still need to look at the nameplate of your particular unit to see it's rating.A "loop feed" Transformer or "feed thru" bushing could be used for an alternate source of supply, or to feed another transformer. For example, a utility could use the feed thru to feed another transformer instead of running amother drop from a pole. In the pic, the two bushings are common.
I am still not sure of a few things about tranny designations in general. Look at this text from the link pv noob posted
High-Voltage Ratings 4160GrdY/2400 through 34500GrdY/19920 or
2400/4160Y
Does 4160grdY/2400 mean it's a 2400 volt primary with one bushing? I assume so. So what does 2400/4160Y mean? 2400 volt but 2 bushings?