K kjroller Member Location Dawson Mn Occupation Master electrician Apr 15, 2025 #1 As long as I have a OCPD my feed for my primary conductors on a transformer can be any length correct?
As long as I have a OCPD my feed for my primary conductors on a transformer can be any length correct?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 15, 2025 #2 correct. If the disconnect is not in sight from the transformer it must be lockable (450.14)
C CoolWill Senior Member Location Alabama Occupation Electrical Contractor Apr 15, 2025 #3 Didn't you just ask this question?