For a 225 kVA transformer 480V delta primary, what size conductors are required with a primary OCPD at 350A (125% of FLA = 338 amps) fed from a distribution panel upstream.
Assuming noncontinuous loads, the transformer feeder minimum size would need to be sized at 100% of the transformer FLA = 270A = 300 kcmils (285 ampacity @ 75 degrees).
However, since the transformer OCPD sized is 350A, the conductors need to be protected in accordance with their ampacity.
But, the next size up rule applies, still applies.
So would 350 kcmils (310 ampacity @ 75 degree), 400 kcmils (335 ampacity @ 75 degree), or 500 kcmils (380 ampacity @ 75 degree) be required?
Assuming noncontinuous loads, the transformer feeder minimum size would need to be sized at 100% of the transformer FLA = 270A = 300 kcmils (285 ampacity @ 75 degrees).
However, since the transformer OCPD sized is 350A, the conductors need to be protected in accordance with their ampacity.
But, the next size up rule applies, still applies.
So would 350 kcmils (310 ampacity @ 75 degree), 400 kcmils (335 ampacity @ 75 degree), or 500 kcmils (380 ampacity @ 75 degree) be required?