Transformer Primary Conductors (for above 1000V)
mshields
Boston, MA
For a typical substation transformer, I was thinking that they could be 125% of FLA even when the primary OCPD was something greater. This would by the defiunition of a tap be just that, a tap. And yet while secondary conductors are covered in the tap rules 240.21, I don't see anything about primary conductors. Bottom line: Do transformer primaries need to be fully rated for the primary OCPD?
Generally yes, transformer primary conductors are protected at there ampacity just like any "normal" conductor. There is However a provision to supply a transformer with a feeder tap, see 240.21(B)(3). I have never used this rule.
Also keep in mind for MV transformers, the feeder supplying the transformer must be rated for the nameplate FLC.
Above 1000V, the transformer primary conductors are only required to be 100% of the primary rated current. The primary OCPD can be greater than primary conductor ampacity. It is not a tap.
Above 1000V . . . The primary OCPD can be greater than primary conductor ampacity. It is not a tap.
So why does 240.101(A) allow a fuse up to 3 times the ampacity, or a breaker with long time trip setting up to 6 times the ampacity? What's the philosophy here?
Thanks, Wayne