Referencing table 450.3B and primary protection. Assuming you use the maximum 250% allowance for your device rating, how are you calculating the primary conductors? Are they still sized at 125% assuming a continuous load since the primary device at that point is short circuit protection? OR do you match the conductors to the device?
15kVA 480V/120-208V poly phase transformer
15*1000/480*1.73 = 18.1A
18.1 *2.5 = 45.25 (can we round up here??) using a 50A primary protective device?
assuming terminations are 75 degree rated
18.1*1.25 = 22.6 so we could use 10awg
OR
matching the device at 250% so 8awg??
NEC references appreciated.