M mjc1060 Senior Member Nov 18, 2020 #1 I am working on an EV panel for a multi-family commercial garage. The feed for the 75KVA transformer is on the first floor. Does the transformer require a local disconnect that is in sight of the transformer?
I am working on an EV panel for a multi-family commercial garage. The feed for the 75KVA transformer is on the first floor. Does the transformer require a local disconnect that is in sight of the transformer?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 18, 2020 #2 No but it is required to be labeled as to the location of the disconnecting means for the primary.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Nov 18, 2020 #3 See section 450.14 in the NEC.
M mjc1060 Senior Member Nov 18, 2020 #4 tom baker said: See section 450.14 in the NEC. Click to expand... Thank You