S steve holt Member Location Hawaii Sep 7, 2018 #1 Do dry type three phase 480v Delta / 208v Wye transformers require a disconnecting means within sight?
Do dry type three phase 480v Delta / 208v Wye transformers require a disconnecting means within sight?
Buck Parrish Senior Member Location NC & IN Sep 7, 2018 #2 Yes , but if you have a locable disconnect upstream like from the feed, then no. Other then class 2 and 3 . 450.14
Yes , but if you have a locable disconnect upstream like from the feed, then no. Other then class 2 and 3 . 450.14