In a recent thread there was a brief discussion of the code rules as far as the sizing of the OCPD that protects the conductors. The example was a 112.5kva 480/208Y/120 transformer with a primay FLA of 135 amps, 1/0 primary conductors and a 300 amp OCPD.
It is my postition that there are no code provisions that would permit you to protect the 1/0 primary conductors above their ampacity. If you want to use a 300 amp OCPD to protect the primary side of the transformer as permitted in 450.3(B) you would have to increase the size of the primary conductors to 300 kcmil.
It is my opinion that the overcurrent protection rules in Article 450 apply only to the protection of the transfomer itself and you have to look to the rules in Article 240 for the protection of the primay and secondary conductors.
It is my postition that there are no code provisions that would permit you to protect the 1/0 primary conductors above their ampacity. If you want to use a 300 amp OCPD to protect the primary side of the transformer as permitted in 450.3(B) you would have to increase the size of the primary conductors to 300 kcmil.
It is my opinion that the overcurrent protection rules in Article 450 apply only to the protection of the transfomer itself and you have to look to the rules in Article 240 for the protection of the primay and secondary conductors.