I recently was asked to install a single phase 50 KVA 480/240 volt transformer. The 600 amp 480/277 panel board has a max breaker limit of 125 amps. Primary amps of 50 kva = 104 x 1.25 = 130 amps required primary OCPD. Dropping down to 1.20 comes in. At 124.8 amps. Is there any way to make this work? With the equipment in place