the amount of current at the secondary is the ratio of the number of turns to the current in the primary. so if there is an overcurrent in the secondary it will be reflected to the primary and the primary OCPD can open.
it doesn't work if there is a neutral involved but as long as it is a delta system or a 2 wire single phase system it works,
personally I don't like it because you have to protect the primary at a relatively low level (125%) and sometimes that can cause nuisance tripping.