I am a little confused on Primary OCPD for transformers, and I tend to second guess myself when questioning an engineered set of transformer/panel schedules. My understanding is Primary OCPD must be sized according to 125% of FLA of your transformer. I believe in certain cases you can or maybe even are required to round down to the next breaker size. But regardless that would still be based off of 125% of Primary FLA according to the nameplate of the transformer, correct?
In my case I have a 45kVA 480 - 208Y/120 xfmr with a FLA on the nameplate of 54A, call it T1. According to the drawings they want to feed with a 50A breaker, 3-#6 and #10 ground (Cu). According to the secondary side load calc I was provided, there will only be about 15A per phase, so I understand the load on this panel is low but something still feels off. Secondary side is feeding a 150A MCB panel, with 4-2/0 and #2 SSBJ (AL).
Not too sure why they called for aluminum on every secondary side xfmr, when the whole building is fed off copper, but that is beside the point I suppose.
What is throwing me for a loop is the panel that is feeding T1 is also feeding a 30kVA 480 - 208Y/120 transformer in the adjacent room, call it T2, with a Primary OCPD of 70A. Fed by 3 - #4 and #8 ground (Cu). The secondary side of xfmr T2 is feeding a 100A MCB panel with 4 - #1 and #4 ground (Al). Calculated load for secondary side of T2 is only 5A per phase. It's a new construction manufacturing facility with planned provisions for future additions and manufacturing lines.
My gut is telling me the breakers need to be swapped.
T1 - 54 x 1.25 = 67.5 --> 70A Primary OCPD.
T2 - 36 x 1.25 = 45A --> 50A Primary OCPD.
My boss has insisted I install it as written on the plans so I am kind of in a pickle as he is seemingly trying to avoid sending an RFI as I suggested. Part me thinks I am making a mountain out of a mole hill, but it has been bugging me for weeks now and the other part is telling me not to energize until I have an answer. Anyways I apologize if any of this is confusing or poorly worded. I respect the heck outta this forum and I appreciate any and all feedback. Thanks for your time.
In my case I have a 45kVA 480 - 208Y/120 xfmr with a FLA on the nameplate of 54A, call it T1. According to the drawings they want to feed with a 50A breaker, 3-#6 and #10 ground (Cu). According to the secondary side load calc I was provided, there will only be about 15A per phase, so I understand the load on this panel is low but something still feels off. Secondary side is feeding a 150A MCB panel, with 4-2/0 and #2 SSBJ (AL).
Not too sure why they called for aluminum on every secondary side xfmr, when the whole building is fed off copper, but that is beside the point I suppose.
What is throwing me for a loop is the panel that is feeding T1 is also feeding a 30kVA 480 - 208Y/120 transformer in the adjacent room, call it T2, with a Primary OCPD of 70A. Fed by 3 - #4 and #8 ground (Cu). The secondary side of xfmr T2 is feeding a 100A MCB panel with 4 - #1 and #4 ground (Al). Calculated load for secondary side of T2 is only 5A per phase. It's a new construction manufacturing facility with planned provisions for future additions and manufacturing lines.
My gut is telling me the breakers need to be swapped.
T1 - 54 x 1.25 = 67.5 --> 70A Primary OCPD.
T2 - 36 x 1.25 = 45A --> 50A Primary OCPD.
My boss has insisted I install it as written on the plans so I am kind of in a pickle as he is seemingly trying to avoid sending an RFI as I suggested. Part me thinks I am making a mountain out of a mole hill, but it has been bugging me for weeks now and the other part is telling me not to energize until I have an answer. Anyways I apologize if any of this is confusing or poorly worded. I respect the heck outta this forum and I appreciate any and all feedback. Thanks for your time.