I am having a debate with our company's Electrical Engineer. Truth be told, I am NOT an engineer, but I have been I/E doing design work for 13 years and have designed numerous transformer installations, as well as MCCs, Pump motors, Lighting, etc., so I know what I'm doing. I feel that he thinks that since he's an Engineer, he knows all and doesn't agree with me at all.
We have a 45kVA transformer with 480V 3P primary and a 240/120V secondary.
The primary is coming off a Square D Series 6 MCC Vertical section, feeding the transformer, and the secondary is going to a 120/240VAC electrical panel with a main breaker on the incoming side.
Sizing the primary is easy...45,000/480/1.732=54.12A...54.12A*1.25=67A. NEC says use the 70A as the next size up standard size breaker.
Sizing the secondary is the same...45000/240=187.5A...187.5*1.25=234A. NEC says use 250A as the next standard size up.
Here's where the debate comes in.
NEC table 450.3(B) shows that if the transformer has protection on the primary AND secondary, the primary OCPD is 250%. He is making me size the primary OCPD at 135A (he said use a 125A), as if it is required. I know it's "up to" 250%, but can't find in the NEC where it says that. He always goes to the highest possible rating in the NEC and doesn't take industry standard into account.
Sorry to vent, but if someone could point me to the NEC where it shows that the 250% OCPD rating is optional, it would help me win this argument.
We have a 45kVA transformer with 480V 3P primary and a 240/120V secondary.
The primary is coming off a Square D Series 6 MCC Vertical section, feeding the transformer, and the secondary is going to a 120/240VAC electrical panel with a main breaker on the incoming side.
Sizing the primary is easy...45,000/480/1.732=54.12A...54.12A*1.25=67A. NEC says use the 70A as the next size up standard size breaker.
Sizing the secondary is the same...45000/240=187.5A...187.5*1.25=234A. NEC says use 250A as the next standard size up.
Here's where the debate comes in.
NEC table 450.3(B) shows that if the transformer has protection on the primary AND secondary, the primary OCPD is 250%. He is making me size the primary OCPD at 135A (he said use a 125A), as if it is required. I know it's "up to" 250%, but can't find in the NEC where it says that. He always goes to the highest possible rating in the NEC and doesn't take industry standard into account.
Sorry to vent, but if someone could point me to the NEC where it shows that the 250% OCPD rating is optional, it would help me win this argument.