For the simplest case of an idealized single phase transformer with 2-wire primary and secondary, and linear loads, the primary current will be a real constant times the secondary current, according to the turns ratio. NEC 240.4(F) therefore allows a primary side OCPD to be used for protecting the secondary conductors accordingly.
What happens if the secondary is replaced with a 3-wire center tapped coil? Suppose the turns ratio is 1 for simplicity, since that captures the new behavior. For a given current on the primary coil, I believe the worst case, in terms of large secondary currents, is that all of the load is connected to one-half of the secondary coil, so the secondary current is twice the primary current. Is that correct?
I'm assuming there are no power sources connected directly to the secondary circuit; otherwise, I believe you can generate power source / load pairs that give you zero current on the primary, so the secondary current could be arbitrarily large, given only a cap on primary current.
Then with those assumptions, it seems like a 240.4(F)-type allowance would be that the primary OCPD could protect the secondary conductors, as long as we use twice the primary OCPD value for sizing the secondary conductors. Yes?
Of course, to do this in practice, in addition to needing NEC allowances that are absent, we'd need a special transformer whose secondary coil is sized to handle all of the power on just half of the coil.
Thanks,
Wayne
What happens if the secondary is replaced with a 3-wire center tapped coil? Suppose the turns ratio is 1 for simplicity, since that captures the new behavior. For a given current on the primary coil, I believe the worst case, in terms of large secondary currents, is that all of the load is connected to one-half of the secondary coil, so the secondary current is twice the primary current. Is that correct?
I'm assuming there are no power sources connected directly to the secondary circuit; otherwise, I believe you can generate power source / load pairs that give you zero current on the primary, so the secondary current could be arbitrarily large, given only a cap on primary current.
Then with those assumptions, it seems like a 240.4(F)-type allowance would be that the primary OCPD could protect the secondary conductors, as long as we use twice the primary OCPD value for sizing the secondary conductors. Yes?
Of course, to do this in practice, in addition to needing NEC allowances that are absent, we'd need a special transformer whose secondary coil is sized to handle all of the power on just half of the coil.