Transformer primary & secondary OCPD

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
If you decide to use both, there’s nothing wrong with putting 125% on both right? Not sure what the purpose would be to put 250% on the primary and 125% on the secondary, just seems more intuitive to put 125% on both.
 
If you decide to use both, there’s nothing wrong with putting 125% on both right? Not sure what the purpose would be to put 250% on the primary and 125% on the secondary, just seems more intuitive to put 125% on both.

No problem with that.
 
If you decide to use both, there’s nothing wrong with putting 125% on both right? Not sure what the purpose would be to put 250% on the primary and 125% on the secondary, just seems more intuitive to put 125% on both.

some people like the higher OCPD setting on the primary to account for the inrush current when energizing the transformer. The disadvantage is you then need larger conductors. I dont recall ever having an issue with 125%.
 
If you decide to use both, there’s nothing wrong with putting 125% on both right? Not sure what the purpose would be to put 250% on the primary and 125% on the secondary, just seems more intuitive to put 125% on both.

In a critical application, I've found it too risky with newer DOE2016 efficient transformer inrush to be as low as 125% on the primary. I usually go to 150% minimum, unless the transformer and breakers come from the same source they they pick it. Schneider tests their combinations, so those are fine.
 