I got a call late today, The customer just had a commercial appliance tech tell him that he has a "voltage problem". The complaint was low voltage at the oven @ 180 volts 2-Pole single phase. I stopped in to take a quick look, I measured the voltage to the panel supplying the oven and found 114/109/115 to phases AB&C to ground respectively and about 196 volts between phases which is higher than the appliance tech measured 4 hours earlier. The oven is name plated for 208 single phase and is connected to legs B&C. There is a 45KVA 480D to 120/208Y transformer supplying the tenant space and the primary side of the txfrmr reflected the same voltage difference on "B" phase. Could this be a simple primary tap change on B phase? I am going back early tomorrow morning to dump the panel and test the transformer voltages with no loads, then turn the loads on 1 at a time while metering the load on "B" phase.