housemoney
Member
- Location
- Midwest
- Occupation
- Engr
Client maintenance guy called and said an existing 480: 120-/240V 10kVA single phase transformer (maybe 15A load) is hot enough to cook eggs on. It's fed from 850' feeder- 60A/480V breaker upstream (AWG unknown). Feeder has about 35A 480V load on it + the 15A of single phase.
My first thought was bad transformer but Is it possible voltage drop on the #6AWG primary feeder at this distance is causing higher secondary current on the the transformer to overheat it?
My first thought was bad transformer but Is it possible voltage drop on the #6AWG primary feeder at this distance is causing higher secondary current on the the transformer to overheat it?